In the Pcs7 system, the analog signal (4-20ma) circuit for the instrument is open circuit – why does the DCS show a maximum value? Shouldn’t it be the minimum?

2020-01-19View Original

Thread Content

As the title suggests, is there anyone who can help answer this? Thank you!
Reply #22020-01-19
It is possible to set it to indicate maximum/minimum values in the case of an open circuit or fault, or to retain the value measured before the fault occurred
Reply #32020-01-20
The answer is above – it can be set manually. Options include fault indication, display of maximum and minimum values, or keeping the values as they are; some systems even allow for more detailed customizations
Reply #42020-01-20
The background configuration allows setting whether to use the larger or smaller value in case of a fault.
Reply #52020-01-21
This can be set; is the original poster just starting to work with DCS?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.