The on-site gauge of the Yokogawa Worm Gear Flow Meter shows a reading, but there is no signal output

2018-08-21View Original

Thread Content

This post was last edited by Clouds in the mist/love on 2018-8-21 at 17:13. The on-site display of the Yokogawa DY040 vortex flowmeter shows a value of 8 cubic meters per hour; its range is 0–30 cubic meters. However, there is no signal output – the measured current is only 1.7 mA, and the voltage is 23.6 VDC. What could be the problem?
Reply #22018-08-21
This circuit should be a 4-wire system; if you measure 23V, it’s likely that the output current wires are connected incorrectly. Or a surge; a damaged safety barrier causes an open circuit.
Reply #32018-08-22
The last edit to this post was made by 955559 on 2018-8-22 at 13:39. 1. Fault symptoms: The vortex flowmeter shows no display when powered on, and it emits no signal. Possible faults: 1) Insufficient power supply to the instrument’s sensor; 2) The flow rate inside the pipeline is too low or there is no fluid flow ; Solution: 1) Check whether the wiring of the instrument sensor is normal ; 2) Locate the valve and open it slowly ; 2. Fault phenomenon: No flow exists in the pipeline of the vortex flow meter, yet the sensor outputs a signal ; Possible faults: 1) Poor grounding of the vortex flow meter results in 50Hz frequency interference ; 2) Excessive vibration in the pipeline where the vortex flow meter is installed ; 3) The sensor gain of the instrument is high ; Solution: 1) Re-ground the instrument ; 2) Strengthen the pipeline in a triangular pattern, and then reinforce it at a 2D distance upstream of the vortex flow meter ; 3) Adjust the sensor’s gain to an appropriate value ; 3. Fault symptoms: Large fluctuations in the flow meter reading. Possible faults: 1) Excessive vibration in the pipeline where the vortex flow meter is installed ; 2) The sensitivity of the vortex flow meter is set too high ; 3) Damaged circuit board ; 4) Large pressure fluctuations ; 5) The vortex sound generator has attachments ; Treatment method: 1) Strengthen the pipeline in a triangular pattern, and then reinforce it at a 2D distance upstream of the vortex flow meter ; 2) Reduce the sensitivity of the instrument ; 3) ) Replace ; 4) Measure the pressure and adjust it to the normal value ; 5) Clean the vortex generator of the vortex flow meter ; 4. Fault symptoms: Large error in vortex flowmeter readings. Possible faults: 1) The distance between the straight sections upstream and downstream of the vortex flowmeter does not meet the required standards ; 2) The instrument constant of the vortex flow meter is set incorrectly ; 3) Attachments upstream of the vortex sound generator ; Solution 1): Change the installation location and select a new installation site as required by the instructions ; 2) Recalibrate the instrument constants of the vortex flow meter ; 3) Clean the vortex generator of the vortex flow meter ;
Reply #42018-08-22
Is it because the transmission distance is too long and the voltage is insufficient?
Reply #52019-12-10
OP, was this issue resolved later? What’s the reason?
Reply #62019-12-11
Yokogawa’s vortex flowmeters are all two-wire type; where did you learn that they are four-wire type?
Reply #72019-12-11
It is very likely that there is a poor connection somewhere in the circuit, resulting in too high an impedance. Or there is a leakage in the circuit of the instrument.
Reply #82019-12-14
Has it been solved? If it’s resolved, please let me know the cause of the fault

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.