How to replace a functioning card assembly

2020-03-01View Original

Thread Content

As title: The Tricon card was replaced online when it malfunctioned; PASS—Active—Completed. So I have this question: for example, suppose an AO card is not faulty and we just need to replace it with a new one. So after inserting a card of the same model into the 1:1 redundant slot and passing the check, is the next step to wait for the scheduled switch-over before removing the old card? Are there any other methods? A beginner seeking advice here
Reply #22020-03-01
No, TRICON does not have a forced soft switch function like some DCS redundant cards.
Reply #32020-03-01
The ICS card holder was replaced a long time ago; it is possible to force a switch of the card holder by mechanically fixing a clip to it. So it’s not known whether Kangjisen has such a function
Reply #42020-03-01
Can’t you just pull out the active card directly?
Reply #52020-03-01
【Reply to Floor 4】 I think the same way; we can only try this again when there’s a suitable opportunity. So check the forum to see if any peers have done it.
Reply #62020-03-02
Since it is a redundant AO card, removing the one that is in use will automatically switch to the backup card. However, this should not be done during normal production, as no one wants to take responsibility if the switch fails and causes a production accident. Forcing a switch is a foolproof method to do during shutdown.
Reply #72020-03-02
After confirming with the manufacturer and conducting production checks, the risk is assessed as low; procedures can be completed and then consideration can be given to proceeding. Be sure to conduct relevant tests under safe conditions such as when parking, in order to gain experience
Reply #82020-03-02
The TRICON maintenance manual strictly prohibits removing the ACTIVE card.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.