Process Engineering Division – Instrumentation and Automation Section – Daily Question – Question from 2020-10-19: Discussion question: 270. When an electromagnetic flowmeter is in operation and its signal becomes progressively weaker or drops suddenly, what could be the possible reasons? How to deal with it?
Reply #22020-10-19
The first reason is that, regardless of the type of flow meter, pipe blockage can lead to a reduced flow rate or no flow at all. For electromagnetic flowmeters, it may also be caused by insufficient power supply to the magnetic induction coil or no power at all.
Reply #32020-10-19
1. There is indeed no data left; 2、There is a problem with the excitation ; 3. The pipe is blocked
Reply #42020-10-19
1. Process-related issues: no medium is arriving, or the medium that arrives is not the correct one. 2. The electrodes are dirty and need to be cleaned. 3. The electrodes have been corroded. 4. There is a fault with the circuit board
Reply #52020-10-19
1. If dirt has accumulated on the inner wall of the measurement conduit, it should be replaced; 2. The signal socket may be corroded and should be cleaned or replaced; 3. The lining of the measurement conduit may be damaged and should be replaced.
Reply #62020-10-19
(1) If dirt has accumulated on the inner wall of the measurement conduit, it should be replaced; (2) The signal socket may be corroded and should be cleaned or replaced; (3) The lining of the measurement conduit may be damaged and should be replaced.
Reply #72020-10-19
1. Dirt may have accumulated on the inner wall of the measurement conduit, and it should be replaced; 2. The signal socket may be corroded, and it should be cleaned or replaced; 3. The lining of the measurement conduit may be damaged, and it should be replaced.
Reply #82020-10-19
1. The electrodes are contaminated or damaged; check the electrodes. 2. There is electromagnetic interference in the vicinity; eliminate the source of interference. 3. The grounding wire has come loose; re-establish grounding. 4. The control valve downstream of the flow meter is faulty; inspect and fix the issue with the control valve. 5. Abnormal operating conditions
Reply #92020-10-19
(1) If dirt has accumulated on the inner wall of the measurement conduit, it should be replaced; (2) The signal socket may be corroded and should be cleaned or replaced; (3) The lining of the measurement conduit may be damaged and should be replaced.
Reply #102020-10-19
1. If dirt has accumulated on the inner wall of the measurement conduit, it should be replaced; 2. The signal socket may be corroded and should be cleaned or replaced; 3. The lining of the measurement conduit may be damaged and should be replaced.
Reply #112020-10-19
1. If dirt has accumulated on the inner wall of the measurement conduit, it should be replaced; 2. The signal socket may be corroded and should be cleaned or replaced; 3. The lining of the measurement conduit may be damaged and should be replaced.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.