Process Engineering Division – Instrumentation and Automation Section – Daily Topics – Topic No. 2020-12-13: Discussion topic: 325. There is a pressure with a range of 320–360 KPa. If measurements are taken using the two pressure transmitters A and B listed below, which one will provide more accurate readings under normal conditions? Pressure transmitter A: Class 1, 0-600KPa ; Pressure transmitter B: Class 1, 250-500 KPa (5 points for the correct answer only; additional points for a correct calculation process or detailed explanation)
Reply #22020-12-14
When using transmitter A, the maximum error in the measurement value is: δmax = ±1% × (500 – 0) = ±5 Kp. When using transmitter B, the maximum error in the measurement value is: δmax = ±1% × (500 – 250) = ±3 Kpa. Therefore, transmitter B provides higher measurement accuracy.
Reply #32020-12-14
Pressure transmitter B has a range of only 250 Kpa – how can it be used to measure pressures above 320 Kpa? ? So, only pressure transmitter A can be selected here for measurement.
Reply #42020-12-14
Pressure transmitter B: Class 1, 250-500KPa
Reply #52020-12-14
Pressure transmitter A: Class 1, 0–600 KPa, with an allowable error of ±6 kPa; Pressure transmitter B: Class 1, 250–500 KPa, with an allowable error of ±2.5 kPa; Therefore, pressure transmitter B provides more accurate measurements.
Reply #62020-12-14
Pressure transmitter A: Class 1, 0–600 KPa, with a measurement error range of ±6 kPa; Pressure transmitter B: Class 1, 250–500 KPa, with a measurement error range of ±2.5 kPa; Therefore, pressure transmitter B provides more accurate measurements.
Reply #72020-12-14
Pressure transmitter B: Class 1, 250-500KPa
Reply #82020-12-14
B also has a precision error of 1%; the error of the B transmitter is 2.5 kPa, which is a small error
Reply #92020-12-14
When using transmitter A, the maximum error in the measurement value is: δmax = ±1% × (500 – 0) = ±5 Kp. When using transmitter B, the maximum error in the measurement value is: δmax = ±1% × (500 – 250) = ±3 Kpa. Therefore, transmitter B provides higher measurement accuracy.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.