2020-12-14View Original

Thread Content

We are responsible for the general contracting work; the solenoid valves provided by the general contracting company are ASCO’s EFG531H301MO models, which do not come with explosion-proof wiring boxes. An explosion-proof sleeve is used to connect them to the transmitter. Is this in compliance with safety standards? Does it also have explosion-proof properties?
Reply #22020-12-14
Saying \"explosion-proof\" is too general; there are many types of explosion-proof designs, and it is necessary to determine which type you have in order to decide whether it meets the requirements. However, solenoid valves are generally flameproof. In the case of flameproof design, according to the principles of flame protection, there is no explosion-proof sealing joint at the connection point between the flexible tube and the solenoid valve; it is possible to use a flexible tube with such a joint, or one can purchase one separately – having that joint will meet the requirements.
Reply #32020-12-14
There’s no problem with that. What is your explosion protection zone? What explosion protection standard is required? Position feedback is an explosion-proof junction box. It’s not that an explosion-proof feature necessarily requires an explosion-proof junction box on the solenoid valve.
Reply #42020-12-14
Could you explain in more detail why? I’ve actually seen this situation where the solenoid valve is connected directly to such a limit switch by a single wire; I was quite puzzled at the time, wondering if it was connected incorrectly
Reply #52020-12-14
Zone 2 explosion protection; solenoids and indicators are connected using explosion-proof flexible tubing
Reply #62020-12-14
Skipping one junction box and one solenoid valve can save 300 to 400 yuan
Reply #72020-12-14
For Zone 2 explosion protection, EXDIIBT4 is sufficient. The plan is to use explosion-proof flexible tubing to connect the solenoid valve and the indicator; in theory this should provide explosion protection, but it’s not clear whether the safety authorities will approve it
Reply #82020-12-15
For explosion protection, as long as both ends have sealed connectors, it’s fine if the wires in the middle are exposed. It seems that the people from the safety supervision agency don’t check things that closely either; they can’t even notice the absence of a couple of connectors
Reply #92020-12-15
Oh, thanks, big guy :handshake
Reply #102020-12-18
The Emergency Management Bureau doesn’t understand this; the experts it sends for inspections come with specific criteria, and anything that doesn’t meet those standards is rejected.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.