2020-12-28View Original

Thread Content

Last night, during the night shift, the position of one pressure-controlled valve remained at 100. Upon arriving at the site, the Siemens locator panel indicated that the input signal was 0 (the signal provided from the control room); this meant the control valve should be in the fully closed position, yet the valve’s position indicator showed it to be fully open. In fact, the valve was indeed fully open on site. The air supply pressure to the locator was normal, but the locator’s output was at its maximum level. After the air supply was cut off, the valve closed completely and did not get stuck. After it was automatically adjusted, the locator worked properly (although the adjustment time was a bit long, especially for the first step). Subsequently, the valve functioned normally. I would like to ask the experts: where does the fault in the locator lie?
Reply #22020-12-28
I’m sorry; the image is not very clear due to the lighting on site. This should be from the calibration process
Reply #32020-12-28
Is Mo Ming having a seizure? :lol:lol:lol:lol
Reply #42020-12-28
The investigation operator reviews the operation change records for that valve level
Reply #52020-12-28
It’s so strange; just make a self-diagnosis and that’s it: lol
Reply #62020-12-28
It seems that the positive and negative feedback of the valve positioner is being impaired
Reply #72020-12-28
In such a situation, first measure the MA value on site; if it is 4MA and the valve shows to be fully open, then the action direction of the actuator is reversed, and it needs to be adjusted. But you said just adjust it, and then trouble arose!
Reply #82020-12-29
The parameters inside the locator should be checked first; it’s the last step during self-testing.
Reply #92020-12-29
Such issues can only be determined on-site; when a problem occurs, what is the current level at the site? Is the air pressure 5 kilograms, and is the valve position feedback resistor functioning properly?
Reply #102020-12-29
In such a situation, it is first necessary to determine the valve positions corresponding to 4mA and 20mA at the site, and then check those in the control room to see if they match. In the case described by the poster, it is very likely that the values do not match; perhaps the operator in the control room made some changes earlier, and then changed them back after you carried out the adjustments
Reply #112020-12-29
Thank you all for your advice. Next time, I will first measure the input current, then check the controller configuration, and finally discuss things with the control room to finalize everything

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.