The Turck 24V proximity switch is installed in an explosion-proof area

2021-04-27View Original

Thread Content

The programmable valve is equipped with a Turck 24V proximity switch, which is located in an explosion-proof area. Is it necessary to install a safety barrier on the DCS? The manufacturer says that a 24V proximity switch does not require such a barrier, while one is needed for 8V switches – is that correct?
Reply #22021-04-27
A 24V proximity switch is definitely not intrinsically safe; using a safety barrier is of no use either. It can only be designed in an explosion-proof format. If it has explosion protection, then it can be used in explosive areas; otherwise, one needs to check whether it can still be used.
Reply #32021-04-27
Just check the explosion-proof marking on the instrument; an “ia” designation is required
Reply #42021-04-27
Use flame-proof ones; flame-proof types do not require safety barriers
Reply #52021-04-27
First, check whether the proximity switch has an explosion-proof mark; if not, it cannot be used regardless of whether a safety barrier is installed or not

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.