A combustible gas detector for measuring methane was installed on site. If the signal sent to the DCS is a 4-20mA signal, how should the range of the DCS instruments be set?
Reply #22021-05-17
0-4mA, 100-20mA, classified according to a linear relationship
Reply #32021-05-17
Of course, it has to be determined based on the output range of the instrument.
Reply #42021-05-17
0-100% LEL corresponds to 4-20 mA
Reply #52021-05-17
Generally, the maximum range is set to twice the lower limit of the explosion limit; this ensures accuracy in measurements below the explosion limit as well as accuracy in measurements above it
Reply #62021-05-18
One cannot focus only on the results. Understand the meaning of the LEL unit, and you’ll understand everything.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.