Seeking help with Yokogawa vortex flowmeter issues

2021-07-14View Original

Thread Content

The company has a Yokogawa split-type vortex flow meter used for measuring high-pressure steam. After it was installed, flow readings were displayed; however, there was no steam in the pipeline and no vibrations as well. When checking the frequency with the meter’s display, a value of around 50HZ was detected. Replacing the converter and the dedicated connection cable did not solve the problem, nor did grounding the sensor’s casing. Has anyone encountered this issue? Is it possible that the sensor is damaged?
Reply #22021-07-14
Generally, new flowmeters do not take sensor failures into account; it is likely that the voltage setting for the frequency is too low. There should be a parameter that can be adjusted for this purpose, and it would be advisable to consult the technical staff at Yokogawa for guidance on making the necessary adjustments
Reply #32021-07-14
Hello, it is necessary to consider whether there is any interference from the power supply at the site; it is best to implement power isolation. Also, check whether there are any powerful motors or sources of vibration near where the meter is installed. The quality of Yokogawa’s meters should make them less likely to get damaged
Reply #42021-07-14
Consider adding a moderate flow rate for resection
Reply #52021-07-15
Yes, check if there is any electromagnetic interference
Reply #62021-07-15
The problem has been initially identified as an issue with the power supply of the flow meter
Reply #72021-07-16
Is it a problem with the power module of the flow meter itself, or is it an issue with the power supply?
Reply #82021-07-16
Turn on the air traffic control testing settings and take a look.
Reply #92021-07-16
I tried adding a power isolation module today, but it didn’t work either; it’s not a power issue. I asked the manufacturer, and they said there might be interference from empty tubes in the pipeline
Reply #102021-07-16
Where is air traffic control testing set up? Can it block 50HZ interference?
Reply #112021-07-18
It’s a normal phenomenon; performing small-signal clipping will suffice

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.