The central control system shows LO TRA

2021-07-17View Original

Thread Content

LO TRA occurred in Zhejiang University’s control system
Reply #22021-07-17
Measure the current value of this channel; it should be less than 4mA.
Reply #32021-07-18
If the current is less than 4MA, it is usually due to a broken wire; if it is even lower than 4MA, an ERR message will be displayed
Reply #42021-07-18
TRA stands for broken connection, no signal received; ERR means less than 4mA, or greater than 20mA

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.