Rosemount single flange level gauge is installed at the front of the material pump, and the reading jumps back and forth

2022-07-16View Original

Thread Content

This uses pressure to indirectly measure the liquid level, but the current situation is: Since the liquid level gauge is installed at the front end of the material pump and on the main pipeline, the operation of the material pump has a great impact on the pressure, resulting in inaccurate readings. Is there any good way to ensure accurate measurement values?
Reply #22022-07-17
It’s difficult to do. The flange sizes are different, and I don’t know if the length of the temperature measuring rod can match. The main reason is that the site is in Indonesia, and it is inconvenient to do anything. The leader asked me to adjust it in the PLC program, but the change in the reading will involve the status of the material pump. My opinion is that the inlet of the material pump is turbulent, the change in pressure is uncertain, and it is unrealistic to modify the program.
Reply #32022-07-18
It is feasible to change the temperature and liquid level mentioned above. It doesn't matter if the flange mouth is different. You can add some reducing joints to solve the problem.
Reply #42022-07-18
You can consider installing a 90° measuring elbow in the flange, with the opening facing the direction of liquid inflow from the large tank, and measuring the total pressure to indicate the liquid level. Although there will be slight fluctuations when the pump is running, the amplitude should not be large.
Reply #52022-07-18
You can consider installing a 90° measuring elbow in the flange, with the opening facing the direction of liquid inflow from the large tank, and measuring the total pressure to indicate the liquid level. Although there will be slight fluctuations when the pump is running, the amplitude should not be large.
Reply #62022-07-18
There is stirring in the equipment above. If the stirring force is strong, it will affect the single flange pressure measurement.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.