Sharing of measuring instruments and final component control valves of different SIL levels in the SIS system

2022-09-13View Original

Thread Content

According to specification 50770, for circuits of SIL2 and above, the measuring instruments as well as the final component switches and valves must be separated from the process control system. There’s no problem with that, but I have a question: for circuits of different SIL levels, such as a SIL1 circuit and a SIL2 circuit, can the interlock solenoid valves (which must meet SIL2 standards) be shared? Conversely, can a measuring instrument (meeting SIL2 requirements) be involved in both a SIL1 interlock circuit and a SIL2 interlock circuit at the same time? I kindly ask all the experts to help clarify this.
Reply #22022-09-13
Sure, one measuring instrument can be shared across multiple interlock circuits; As for the actuator, it usually has one output; as long as the several interlock settings do not conflict with each other, that’s fine
Reply #32023-07-08
The higher standard takes precedence; the highest standards are the key.
Reply #42023-07-10
If it’s genuine advice, I’d be more than happy to accept it. If it’s just an act of showing off from a superior position, please read my question first. It was a problem from last year already, and the teacher on the second floor also answered my questions. Thank you all for your replies; please pay more attention to new questions. :lol
Reply #52023-07-10
I’m sorry, I didn’t see it clearly. All I see are new problems{:2_32:} Never mind, I should stop talking; I’m such a talkative person. When I see silly questions, I always feel like reacting to them! Sorry {:2_43:}

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.