I would like to ask the experts: Are self-acting control valves of type FO or FC? Thank you
FO: Fault On FC: Fault Off
There’s no such thing as a failure of the air source in a self-acting type, right? But if there’s no upstream pressure, isn’t the pressure reducing valve fully open?
There is no such concept for self-acting types, as there is no air source
The three disconnections in control valve failures refer to the loss of air supply, power supply, and signal. FO=Fail Open, which means the valve remains open in the event of a failure; FC=Fail Close, meaning the valve remains closed in such a situation. By \"failure\" is meant the interruption of air supply – i.e., what happens when the air supply is cut off, and whether the valve is in an open or closed state. The characteristic of a self-acting control valve is that it can perform regulation without the need for an external air source (by utilizing the pressure of the medium itself); therefore, concepts such as FO and FC do not apply to self-acting control valves.
If it is used to regulate the pressure before the valve, similar to FC; If it is used to regulate the pressure after the valve, similar to FO: lol
Self-acting valves with pressure tapping behind the valve generally operate to close (to stabilize the pressure behind the valve), while self-acting valves with pressure tapping in front of the valve generally operate to open (to stabilize the pressure in front of the valve). Self-acting control valves are not classified as FC or FO; the distinction lies only in whether pressure is taken from inside the valve, from outside the valve, or before or after the valve.