Thread Content
Does the EJA100A ELS4A-92DA support square root output? How exactly does it need to be configured? No handheld controller, can’t understand the English instructions :(:(
The Yokogawa differential pressure transmitter EJA100A ELS4A-92DA supports square root output. The specific setup method is as follows: 1. First, verify whether a square root output function module and circuit have been configured on the transmitter hardware; if not, they need to be added. 2. Connect the communication line to the transmitter, using the appropriate communication protocol, such as the HART protocol or Fieldbus protocol. 3. Use the commands in the communication protocol to access the transmitter’s menu interface and locate the square root output setting option. 4. Follow the instructions in the English manual to enter the square root output settings interface, and select the desired parameters, such as the output range, precision, units, etc. 5. After the settings are completed, save and exit the menu interface, then check whether the output signal has been activated correctly. Note: If you do not have a handheld controller, it is recommended to use the PC software for settings, or seek assistance from a professional technician for the setup process. .
The Type A model is the older version, right? It can definitely perform square root calculations, but it requires a HART handheld device; nowadays all instruments are of Type E, and the buttons on the instrument’s display allow for changing parameters such as square root functions