Where are the measurement points for flue gas temperature and suction?

2019-03-25View Original

Thread Content

For the measurement points of temperature and suction at large chimneys and flue branches, are they generally located before the flap, after the flap, or can either location be used?
Reply #22019-03-25
It can be placed either in front of or behind the flap, but it must be at a certain distance from the flap; this distance is related to the flow velocity, and the measurement should be taken when the airflow is in a steady state.
Reply #32019-03-25
Regarding temperature, there is no significant difference before and after flipping the flap; either position is acceptable. But in terms of suction force, the function of the flap is to regulate this force by changing its opening degree; in other words, the suction force before and after the flap is significantly different. So, which value of suction force should we measure – that before the flap or that after it?
Reply #42019-03-26
Set the measurement point where you want to measure the suction force
Reply #52019-03-28
Question: On the computer in the control room, the total flue suction and temperature values displayed there – where are these readings taken from? Before the flap turns or after? The temperature remains more or less the same; the resistance from replication does not cause much change in temperature ; However, the flap resistance increases the suction force, resulting in a significant difference between the front and back.
Reply #62019-03-30
Question: The main flue of the coke oven here has collapsed and needs to be rebuilt. It’s no longer possible to see the installation location on site, so I would like to confirm with you where exactly the measurement points should be placed.
Reply #72019-03-30
It should be before the flap is flipped, that is, when the smoke has not passed through the area where the flap is located
Reply #82019-05-15
Where there is a hole at the diagonal cross on the temperature side, suction can be applied on the front side, but it must be sealed properly; otherwise, the suction strength will not be accurate
Reply #92019-05-16
I went in to check before flipping the panel. There is no point in placing it behind the flip switch; the suction force of the switch flip switch doesn’t change much.
Reply #102019-05-16
Here, \"front\" and \"back\" refer to the direction of the furnace body as front, and the direction of the chimney as back.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.