Do the electrical ground and the instrument ground need to be connected together?

2018-03-29View Original

Thread Content

As the title suggests, in a factory, should the electrical ground grid and the DCS grounding system be connected together? Some believe that they should not be connected, out of concern that lightning waves from thunderstorms might penetrate into the DCS through the electrical ground grid. Others think they should be connected to prevent potential differences from arising. Please discuss the actual situations in your respective companies and provide your opinions
Reply #22018-03-29
Comply with the \"Code for Design of Grounding of Instrumentation in Petrochemical Industries\" SHT 3081 and the \"Code for Design of Grounding of Instrumentation Systems\" HG/T 20513-2014.
Reply #32018-03-29
Both of these specifications require connection to the electrical ground, unless the resistance of the electrical ground network is greater than 4 ohms
Reply #42018-03-30
From a regulatory perspective, there should be no problem connecting it to the electrical grid. However, I have also seen drawings produced by some DCS manufacturers that separate electrical grounding from instrument grounding. In practice, what I often encounter is that the protected areas are connected to the main grounding grid, while separate grounding piles are used for the instruments.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.