110KV distribution equipment room, SF6 gas emergency exhaust plan

2018-11-22View Original

Thread Content

For 110KV distribution equipment rooms, what is the appropriate scheme for exhaust ventilation in case of SF6 gas leaks? Can ventilation ducts be installed in the distribution room to exhaust air upward to the roof (similar to a range hood, with the intake located 15 centimeters above the ground)? Do we still have to install the fan directly at the bottom of the wall to exhaust it outside?
Reply #22018-11-22
Either one is fine; it’s not specified that it has to be the latter.
Reply #32018-11-22
Thank you! May I ask if ventilation ducts can be installed indoors? Do we still have to walk outside? Also, are there any specific guidelines for the ventilation design related to SF6 accident exhaust?
Reply #42018-11-22
Check the relevant standard GB50035 – it does not specify anything, so it can be used both indoors and outdoors. In GB50059, the ventilation requirement is specified as 2 hours per time under normal conditions, and 4 hours per time in case of an accident; please check again to confirm
Reply #52018-11-23
SF6 is denser than air and tends to accumulate at the bottom; therefore, exhaust fans should be installed at the lower part
Reply #62019-03-05
Thank you! But there’s a problem now. There is no space at the lower part for installing a fan. Outside the wall are other rooms. The lower fan cannot discharge air directly to the outside.
Reply #72019-03-07
Thank you! I think the same way now too.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.