Questions regarding the 35/10KV substation

2019-07-03View Original

Thread Content

If there are no 10kV electrical equipment in the factory, can a 35/0.4kV substation be installed directly to eliminate the need for an intermediate step of voltage transformation? The power supply company says that for factories with a capacity of over 20,000 kW, a 35/10 KV substation is necessary. Is this reasonable? Thank you
Reply #22019-07-04
Select the appropriate voltage level based on the load; it is completely correct to choose a 35 kV voltage level for a 20,000 load. 20,000 – Transformers with a voltage of 35/0.4 kV are extremely large in size; it’s unlikely that any manufacturer produces them. It’s also not possible to use low-voltage power inputs, and the design is unreasonable; this option should not be considered.
Reply #32019-07-08
10/0.4kV substation can be configured
Reply #42019-07-16
I’m honest with you – there are manufacturers that produce them.
Reply #52019-07-16
It’s really hard to say; each specific project needs to be analyzed individually. It’s impossible to give an answer just by mentioning a concept. I’ve really never seen a factory with a capacity of 20 MVA that doesn’t have any 10 kV electrical equipment. Is 35kV used for high voltage? 35/0.4kV transformers are available, but those with a capacity over 4MVA are generally not chosen due to the high low-voltage short-circuit current. For a 20MVA, 35/0.4kV transformer, it’s really hard to figure out how to choose the voltage level for the low-voltage side. If low-voltage equipment is indeed grouped by area, 35/0.4kV transformers for those areas can be used. To go deeper, it is necessary to conduct a comparison of various options and carry out an analysis of economic benefits.
Reply #62019-08-02
35 kV transformers with a capacity of 20,000 units are quite common, but transformers with a low-voltage side of 0.4 kV and a capacity of 20,000 units have indeed never been seen. The current on the low-voltage side of the transformer is nearly 30,000 amperes; how large must the low-voltage windings of the transformer be? ? :o
Reply #72019-11-29
In the areas where various loads are concentrated in locations with 10Kv transformers, the 10KV line losses are much lower than those of low-voltage systems (400V)! In this way, only one 10KV cable is needed to go from 35KV to the substation, thus solving the problem. We arrange it this way; of course, it needs to be considered in its entirety during the overall planning stage! ! !
Reply #82019-11-30
Thank you, I understand. It’s not reasonable to do that.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.