2019-09-10View Original

Thread Content

Substations equipped with oil transformers and oil circuit breakers must be fitted with emergency exhaust fans; Do dry-type transformers and high/low voltage substations still need to be equipped with accident exhaust fans? Which standard clause specifies this?
Reply #22019-09-10
The new standard \"DLT 5725-2015 Code for Construction of Substations for Power Users at 35 kV and Below\" has been found. According to 15.4.1.2, the distribution equipment shall be equipped with emergency exhaust fans that can provide at least 10 air changes per hour; such fans can also be used for normal ventilation purposes.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.