Petrochemical hydrogenation unit

2019-01-04View Original

Thread Content

At the high-hydrogen cut-off point, the on-site magnetic flap matches the remote display. However, when raising the level, both the local reading and the remote reading increase very slowly. If the magnetic flap is removed to allow venting and then reinstalled, the level will change suddenly, with both the local and remote readings changing at the same time (sometimes they both reach the full scale). The same phenomenon occurs when lowering the level. What causes this?
Reply #22019-01-14
We have encountered similar situations; the reason is that dirt has clogged the area where the bottom of the magnetic flap is connected to the equipment
Reply #32019-01-19
This kind of delay also occurs in our system at high level thresholds. As for the reasons behind this, there is no clear answer yet. My speculation is that firstly, there are too many impurities in the interface; in the case of remote transmission using float level gauges, the floats may get stuck. Secondly, the temperature is low after air cooling, especially in winter, which reduces the density difference between oil and water, thereby diminishing the effectiveness of separating them and leading to malfunction in remote transmission. Thirdly, when injecting water at high levels, it is necessary to control the amount of scale and corrosion inhibitors added; excessive use can also result in incomplete separation of oil and water, with oil remaining in the water and causing foaming issues. These are just my personal opinions; I would appreciate it if professional experts could provide their guidance.
Reply #42019-02-24
Using magnetic flip switches on-site isn’t very suitable for measuring liquid levels, is it?
Reply #52019-02-26
First of all, are your on-site magnetic flap switches and remote transmission connected to the same outlet on the gauge? If so, the pipeline is blocked. Previously, the on-site liquid level in our cold high-pressure system was always significantly behind that of the remote unit; after investigation, it was found that the lower part of the on-site level gauge was blocked. Once it was cleaned, the lagging issue no longer occurred.
Reply #62019-02-27
Will the on-site level gauge affect remote transmission? It seems that your level gauge is large enough as well; when it’s put into use, opening the valve will cause a certain impact on the liquid level, and the order in which operations are carried out also has an effect

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.