What are the typical alarm values for high pressure difference at the inlet and outlet of the air cooling tower in an air separation unit, as well as the alarm value for low outlet pressure?

2019-05-08View Original

Thread Content

I would like to ask those with more experience: what are the typical alarm values for high pressure difference at the inlet and outlet of the air-cooled tower in an air separation unit, as well as the alarm value for low outlet pressure? {:3_46:}
Reply #22019-05-12
The design resistance for air-cooled towers is generally 5 kPa; the alarm threshold can be set based on the actual operating values. The outlet pressure of air-cooled towers is usually set with a low-limit alarm at 400 kPa, and an interlock trigger at 350 kPa~~
Reply #32019-05-12
5.0kpa/10.5kpa

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.