Pump reversal causes an overload alarm on the inverter

2020-08-02View Original

Thread Content

Hello, everyone! I have a water supply pump here, a horizontal centrifugal pump with the motor connected directly to it, and it features constant pressure control. Due to a damaged outlet check valve, the pump reverses direction when it stops running. When the pump is in automatic mode, an overload alarm on the frequency converter occurs frequently; this problem did not exist before. The electrician believes that the overload alarm is caused by the pump reversing direction. Has anyone else encountered this issue? I have seen the pump run in reverse before, and there was no overload when it was started directly. Could someone explain this? Not very grateful
Reply #22020-08-02
This is because the torque during direct starting and variable-frequency starting is different, which causes the inverter to give an alarm
Reply #32020-08-02
As the poster said, there’s a problem with the check valve at the outlet – it can’t be closed properly, which causes the pump to run in reverse due to backflow of the fluid!
Reply #42020-08-02
In actual operation, if such problems do arise, it is recommended to change the approach: before shutting down the pump, close the outlet valve first, and then proceed with shutting down the pump, in order to prevent similar situations from occurring and causing damage to the pump, motor, and related components.
Reply #52020-08-03
It would be best to recall the basic electrical concepts from middle school physics, specifically those related to generators and motors; this knowledge might help explain this phenomenon. For reference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.