Why isn’t a vent provided at the top of this expansion joint?

2019-10-12View Original

Thread Content

Isn’t it said that exhaust needs to be released at high points?
Reply #22019-10-13
Generally, a temporary vent valve is installed during pressure testing, and it is removed after the testing is complete. If a vent valve remains in place, it creates an additional point of leakage; it may also be accidentally opened by someone who is not aware of its presence, leading to leaks. Additionally, it facilitates oil theft in the case of oil-based products
Reply #32019-10-13
If it is a gas medium, there is no need to set it either
Reply #42019-10-13
These are most likely steam pipes that haven’t been insulated yet. The exhaust valve seems to be of little use; it’s better not to have it, as operating it can be very dangerous
Reply #52019-10-13
I don’t think it’s a steam pipe; there’s no drain at the lower end.
Reply #62019-10-13
What medium is in the pipeline? ? Gas bar
Reply #72019-10-14
Before using this pipeline for the first time, it needs to be pressure-tested, and this expansion joint can be removed; by removing it and testing each part separately, there is no need to install a vent valve; After normal operation, since the pipeline is a thermal pipeline with a pressure generally above 6 KG, the air inside the pipeline can be completely expelled. Installing an exhaust valve is not only unnecessary but also adds many additional static sealing points, which is utterly redundant.
Reply #82019-10-14
It’s probably the residual gas in this small section; it has little impact on the pressure testing, after all, the pipeline is quite long. Gas dissolves in water under pressure; as the temperature rises or falls, the pressure inside the pipeline increases or decreases relatively quickly, and overpressure may occur. Installing a safety valve can provide protection against this. For a simple check of the weld’s pressure resistance, this high-point venting can be ignored.
Reply #92019-10-14
Agree with the person in floor 3; this is probably just due to thermal expansion and contraction, not exhaust
Reply #102019-10-16
Vent the air during pressure testing; otherwise, there will be air in between

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.