Do combustible and toxic gas alarms need to be installed on the framework of each floor of the facility? Should it still be placed only on the ground? Its density is greater than that of air.
Reply #22015-06-09
Do you mean the setting of alarm values or something else?
Reply #32015-06-09
The setting refers to the number of alarms, not the alarm threshold values.
Reply #42015-06-09
3161148020 My QQ is added; let’s chat there
Reply #52015-06-09
As per the design, this distribution has specific requirements: those with a density greater than that of air should be installed downward, while those with a lower density should be installed upward
Reply #62015-06-09
I mean, does every layer of the multi-layer framework need to be set up? Because every layer could potentially leak, how can this be determined?
Reply #72015-06-09
I don’t know much about design specifications, but for frameworks, in some projects I’ve worked on there was a design that included one per floor; however, I’m not sure about the density of the probes used
Reply #82015-06-10
It must be installed wherever there is a source of release, upwind at the lowest possible frequency; the distance between the combustible gas detection point and the source of release should not exceed 15 m, while the distance for toxic gas detection points should not exceed 2 m.
Reply #92015-06-10
There are safety procedures; **standards have been established**
Reply #102015-06-10
Our device is also available on the 2nd floor, but not on the 3rd floor.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.