Natural gas boiler

2015-07-13View Original

Thread Content

The natural gas heater in our office shuts down on its own whenever it rains or is foggy, and it has to be started manually – it won’t start automatically at all. It’s a vertical unit installed outside. Could anyone give me some advice?
Reply #22015-07-14
This post was last edited by xyc114 on 2015-7-14 09:36; a water film may form in rainy or foggy weather, causing poor contact with the temperature transmitter. Identification method: ignore temperature changes; if the short-circuit signal is present, it can start automatically.
Reply #32015-07-18
Please explain in detail what the first alarm refers to; it could be due to poor insulation in the control system.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.