The voltage supplied by the PLC to the solenoid valve should be 220V, but when the PLC does not output any signal, the voltage is 70V. What is the reason for this?

2015-08-09View Original

Thread Content

During the instrument maintenance yesterday, the cause could not be identified. When the PLC sends an output signal, 220V is generated, which is normal; but why is the voltage 70V when there is no output? All other solenoids have a voltage of 220V when output is active and 0V when there is no output. Please give me some advice, experts
Reply #22015-08-09
Is this 70 you mentioned measured on-site? It is recommended to measure at the cabinet terminals to determine whether the issue lies before the cabinet terminals or in the wiring
Reply #32015-08-09
I think this 70V is an induced voltage; go and measure it at the PLC relay output!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.