Fuel gas pipeline venting issue

2015-09-18View Original

Thread Content

According to the fire protection design codes for petrochemical enterprises, vent pipelines should be located above the operating platforms or building roofs within a 20-m radius. So, does a boiler room with a height of 60 meters count as a building? Must the vent pipeline be higher than the roof of the boiler room? Someone from a design institute asked me whether air could flow back into the vent line when the valve on that line is opened for venting. I haven’t encountered any danger in practice, but how can this issue be explained theoretically? For this reason, the design institute asked me to replace the vent pipeline’s pneumatic cut-off valve with a manual valve, but it seems that this does not solve the problem
Reply #22015-09-18
A boiler room definitely belongs to a building. You can’t continuously release fuel gas into the atmosphere, right? It should only be needed during startup and shutdown. This doesn’t even qualify as “intermittent” emissions; if it did, it would be within a range of 10 meters. Moreover, the wording is “not advisable,” rather than “mandatory.”

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.