Who has dealt with the chain connection of the DCS? It has been removed, but the pump still doesn’t start. Who knows what the reason is?

2015-08-10View Original

Thread Content

This post was last edited by zlky2005 on 2015-8-16 at 16:43. Who has dealt with the cascade in the DCS system? It has been disconnected, but the pump still stops running – who knows why? Thank you!
Reply #22015-08-10
There are many reasons for stopping the pump; is it certain that it is related to interlock conditions and interlock actions?
Reply #32015-08-10
View the control program online to find out what caused the shutdown
Reply #42015-08-10
There are several reasons for the pump stopping here: interlocks in the SIS; BPCS in DCS; overload protection in electrical systems. For reference only.
Reply #52015-08-10
Ask if the electrical equipment has overload and underload protection~
Reply #62015-08-11
Because every time the pump shutdown alarm occurs, it’s due to the liquid level iop, but the interlock for the liquid level has been disabled
Reply #72015-08-11
IOP, then you must be using Yokogawa’s DCS there. Are you doing the interlocking through .ALRM, or through RL comparison blocks? I suggest you upload a screenshot of the specific logic of lc64.
Reply #82015-08-11
It is recommended to start looking for the cause from the electrical side, to trace it back to its origin, by checking each part one by one
Reply #92015-08-15
There is no DCS interlock, but the pump still stops – was it an overcurrent? You can check the operating conditions and the pump itself
Reply #102015-08-15
It is recommended to view the program online via DCS! I don’t know which company’s DCS it is! Watch online: Is the motor stopping caused by a low liquid level of 1? ! Otherwise, find some other reason!
Reply #112015-08-16
Hehe, from my experience: when there are RS flip-flops in the program and the program isn’t complete, it leads to a situation where R=0 and S=0, which in turn triggers something automatically

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.