How is the fire boundary determined for vertical fire-tube boilers?

2015-08-27View Original

Thread Content

How is the fire boundary determined for vertical fire-tube boilers? If the fire level cannot be determined, the position of the water gauge cannot be determined either. I seek advice from those who are more experienced.
Reply #22015-08-28
For the LSG type, it is determined by comparing the top of the furnace chamber with the upper end of the curved water pipe in the smoke box, taking the higher of the two values; the lowest safe water level is 100 mm above the highest fire level.
Reply #32015-09-10
In shell-and-tube boilers, the lowest water level must be 100 mm above the highest fire boundary. For flue tubes such as those used in stack vents, there is no clear definition for the highest fire boundary; generally, it is considered to be the seam around the stack vent.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.