How to calibrate the range of a capacitive transformer?

2015-10-05View Original

Thread Content

How to calibrate the range of a capacitive transformer?
Reply #22015-10-05
Connect the input terminal of the transmitter to a standard pressure source, and the output terminal to a standard ammeter. Enter the standard pressure value corresponding to the upper limit of the transmitter’s input; at this point, the output current of the transmitter will be 20mA. If that’s not the case, adjust the external range potentiometer. Then remove the pressure value; the transmitter will display 4mA. If that’s not correct, adjust the zeroing potentiometer. Next, input the maximum pressure value and check the output current value. Repeat this process a few times to make the adjustment.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.