Is it necessary to equip each pneumatic valve’s intake pipe with a three-piece unit?

2015-10-22View Original

Thread Content

Is it necessary to equip each pneumatic valve’s intake pipe with a three-piece unit? Is it okay to install one on the main pipe? If an solenoid valve box is installed, is it against the specifications to install a three-way fitting on the main pipe?
Reply #22015-10-22
It’s not necessarily the case; some of the air used for instruments in our company goes through specialized drying and oil-removal equipment, so pneumatic triple units are not required when using them.
Reply #32015-10-22
It’s better to add it; after all, the instrument is the eyes of production
Reply #42015-10-22
Does that mean it needs to be added in front of each pneumatic valve?
Reply #52015-10-22
Definitely add it; how much is a triple unit anyway? Control valves are incredibly expensive~
Reply #62015-10-22
If the facility has a common instrument air system, and the instrument air is specially treated, then it may not be necessary to install a triple unit; otherwise, its installation is required.
Reply #72015-10-23
A filter-regulator valve should be installed on the air supply pipeline for pneumatic control valves. For cylinder-type pneumatic on/off valves (without valve positioners), a pneumatic trio should be used, which serves to filter, regulate pressure, and lubricate the cylinder.
Reply #82015-10-23
Sir, what is a valve positioner used for? If I already have it, do I still need to install a three-piece set?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.