YT1000 valve positioner surge

2015-12-03View Original

Thread Content

RT, the valve positioner isn’t working properly. A new YT1000 valve positioner was installed, but it experiences surging during calibration – there’s a hissing sound, and it can’t hold its position when switched on or off. Has anyone encountered this issue? What could be the reasons for this?
Reply #22015-12-03
Has the 4-20ma signal been tested?
Reply #32015-12-03
I don’t know if it’s 1000l or 1000r. In the case of surge, first check whether the air supply pressure is within the acceptable range; also examine whether the springs are fatigued, if there are any issues with the nozzle baffles or nozzles themselves, and whether the diaphragm has aged and is leaking air, among other things. This is assuming there is no problem with the diaphragm of your control valve.
Reply #42015-12-04
If it’s a new locator, check the connection between the locator and the valve body. If it is a double-acting angular stroke type, it could be that the connection between the positioner and the cylinder is in the wrong position or loose.
Reply #52015-12-04
It is possible to enter the locator parameter configuration to adjust the dead zone range, provided that the requirement for control accuracy is not high;

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.