HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

What adjustments are needed on the DCS system while driving?

2015-12-03View Original

Thread Content

Are the PID parameters adjusted only while driving? How to carry out interlock debugging? Is the factor that doesn’t meet the conditions a forced signal that meets the requirements?
Reply #22015-12-03
1. It is best to confirm the forward and reverse actions of the regulator before starting up (discuss this further with the process engineers to ensure that the operation of the control valves is appropriate for the process). A set of empirical values can be used for the PID parameters. 2. All other types of coordination tests can be carried out; of course, you need to reset all the parameters you have set before starting up. It is recommended to work on one circuit or one interlock system at a time, and only after proper testing should the manually set parameters be removed. 3. Ensure that the actual operation of each switch and valve at the site matches what is shown on the DCS, as during programming many elements are similar, and programs are often copied with only the tag numbers changed. There may be some tag numbers that were not replaced accidentally. 4. Go through each flow diagram one by one to conduct a thorough inspection and confirmation
Reply #32015-12-03
Before starting up for the first time, the instruments are calibrated individually first, and then each instrument circuit is calibrated together. After the interconnection is completed, interlock tests are carried out together with processes, electrical engineering, and related specialties. At the beginning of operation, the unit is unstable; it is recommended not to switch to automatic mode for now, so the PID parameters should also not be adjusted at this stage – using empirical values is sufficient. If the condition is not met, a default value must be set first, but be sure to change it back later.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.