【Daily Question】12.24 Requirements for boiler deaeration (3 wealth points for a reply + additional 3–8 wealth points if the answer is correct)

2015-12-24View Original

Thread Content

This post was last edited by lzy4225925 on 2016-1-2 at 10:56. Topic content: Fill in the blanks: The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" requires that the feed water for steam boilers should be ( ). For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, ( ) can also be used; however, it is necessary to closely monitor scaling, corrosion, and water quality in such boilers, and to properly carry out tasks such as chemical dosing, sludge removal, and cleaning. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, if local corrosion is detected, ( ) should be taken. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, ( ) can be used; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, along with proper dosing of chemicals. When the rated power of a hot water boiler is ≥4.2MW, it should ( ), while for hot water boilers with a rated power of <4.2MW, the feed water should ( ). Extracorporeal chemical treatment, in-furnace chemical dosing, deoxidation measures, in-furnace chemical dosing, deoxidation – maximum deoxidation possible. Requirements for answering the question: Answers must be provided in strict accordance with the standard wording. Hint regarding the selection of deoxidation measures: Please note that we will close this thread after 24 hours, during which time the best response (the most helpful answer) will be announced, along with the correct answer and its explanation. Other details: Recruitment for moderators & technicians in the [Mechanical Zone] – applications and referrals are welcome. 【Valid indefinitely】【If you’re interested, come ahead!】 】(Click to enter) 【Mechanical Zone】Comprehensive guide to preventing equipment freezing over during winter 【Mechanical Zone】Call for collection of essential knowledge【Seeking manufacturer sponsors】(Ongoing campaign)【Rewards for recommending valuable content; the “Active Users and Weekly Stars” competition in the Mechanical Zone has begun】Wealth, metals, corrosion, zones, machinery
Reply #22015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" requires that the feed water for steam boilers should be treated (through feed water treatment). For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, in-water chemical treatment can also be used; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, and proper handling of chemical addition, sludge removal, and cleaning must be carried out. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In boilers with a rated evaporation capacity of <6 t/h, deoxidization measures should be taken if local corrosion is detected. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be used; however, close monitoring of scaling, corrosion, and water quality is necessary, and the chemical treatment process must be carried out properly. When the rated power of a boiler is ≥4.2MW, deoxidization is required for such hot water boilers, while for those with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #32015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical treatment should be used for the feed water. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal chemical treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, and proper handling of chemical addition, sludge removal, and cleaning must be carried out. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In boilers with a rated evaporation capacity of <6 t/h, deoxidization measures should be taken if local corrosion is detected. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, (chemical treatment inside the boiler) can be used; however, close monitoring of scaling, corrosion, and water quality in the boiler is necessary, and chemical treatment must be carried out properly. When the rated power of the boiler is ≥4.2MW, hot water boilers should undergo (deoxidization), while for hot water boilers with a rated power of <4.2MW, the feed water should be (deoxidized as much as possible).
Reply #42015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical treatment should be used for the feed water. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal chemical treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality is necessary, and proper handling of chemical addition, waste discharge, and cleaning must be carried out. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, if local corrosion is detected, deoxidization treatment should be applied. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be employed; however, close monitoring of scaling, corrosion, and water quality is necessary, and the chemical treatment process must be carried out properly. When the boiler’s rated power is ≥4.2MW, deoxidization is required for hot water boilers, while for those with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #52015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical treatment should be used for the feed water. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal chemical treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality is necessary, and proper handling of chemical addition, waste discharge, and cleaning must be carried out. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, deoxidization measures should be taken if local corrosion is detected. The oxygen content in the feed water for turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be employed; however, close monitoring of scaling, corrosion, and water quality in the boiler is necessary, and proper chemical treatment must be carried out. When the boiler’s rated power is ≥4.2MW, deoxidization of the feedwater is required for such hot water boilers, while for those with a rated power of <4.2MW, the feedwater should be deoxygenated as much as possible.
Reply #62015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical water treatment should be used for the feedwater. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal chemical treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, and proper handling of chemical dosing, sludge removal, and cleaning must be carried out. Deoxygenation is required when the boiler’s rated evaporation capacity is ≥6 t/h. In boilers with a rated evaporation capacity of <6 t/h, deoxygenation measures should be taken if local corrosion is detected. The oxygen content in the feedwater for turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be used; however, close monitoring of scaling, corrosion, and water quality is necessary, and proper chemical treatment must be carried out. When the rated power of the boiler is ≥4.2MW, deoxidization is required for such hot water boilers, while for those with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #72015-12-24
Extracorporeal chemical treatment, in-furnace dosing treatment, deoxygenation measures; in-furnace dosing treatment is necessary – deoxygenation should be achieved as much as possible
Reply #82015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical water treatment should be used for the feedwater. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal dosing treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, and proper dosing, blowdown, and cleaning procedures must be followed. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, deoxidization measures should be taken if local corrosion is detected. The oxygen content in the feedwater for turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be employed; however, close monitoring of scaling, corrosion, and water quality in the boiler is necessary, and proper chemical treatment must be carried out. When the rated power of a hot water boiler is ≥4.2MW, chemical treatment inside the boiler is required, while for boilers with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #92015-12-24
The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" stipulates that for steam boilers, external chemical treatment should be used for the feed water. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, internal chemical treatment can also be employed; however, close monitoring of scaling, corrosion, and water quality in such boilers is necessary, and proper handling of chemical addition, sludge removal, and cleaning must be carried out. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In boilers with a rated evaporation capacity of <6 t/h, deoxidization measures should be taken if local corrosion is detected. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be employed; however, close monitoring of scaling, corrosion, and water quality is necessary, and the chemical treatment process must be carried out properly. When the boiler’s rated power is ≥4.2MW, deoxidization is required for hot water boilers, while for those with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #102015-12-24
Fill in the blanks: The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" requires that for steam boilers, (outside-the-boiler water treatment) should be used for the feedwater. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, (inside-the-boiler water treatment) can also be employed; however, it is necessary to closely monitor issues such as scaling, corrosion, and water quality, and to properly carry out tasks related to chemical addition, waste discharge, and cleaning. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, if local corrosion is detected, (deoxidization measures) should be taken. The oxygen content in the feedwater for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical dosing inside the boiler can be used; however, close monitoring of scaling, corrosion, and water quality in the boiler is necessary, and proper chemical dosing must be ensured. When the boiler’s rated power is ≥4.2MW, deoxidization is required for hot water boilers, while for those with a rated power of <4.2MW, the feed water should be deoxygenated as much as possible.
Reply #112015-12-24
Fill in the blanks: The national standard GB1576-2001 \"Water Quality for Industrial Boilers\" requires that for steam boilers, (external chemical treatment) should be used for the feed water. For steam boilers with a rated evaporation capacity of ≤2 t/h and a rated steam pressure of ≤1.0 Mpa, (internal chemical treatment) can also be employed; however, it is necessary to closely monitor issues such as scaling, corrosion, and water quality, and to properly carry out tasks related to chemical addition, waste discharge, and cleaning. Deoxidization is required when the boiler’s rated evaporation capacity is ≥6 t/h. In the case of boilers with a rated evaporation capacity of <6 t/h, if local corrosion is detected, (deoxidization measures) should be taken. The oxygen content in the feed water for boilers supplying steam to turbines should be ≤0.05 mg/l. For hot water boilers with a rated power of ≤2.8MW, chemical treatment inside the boiler can be employed; however, close monitoring of scaling, corrosion, and water quality in the boiler is necessary, and proper chemical treatment must be carried out. When the boiler’s rated power is ≥4.2MW, deoxidization is required for such hot water boilers, and deoxidization of the feed water is also necessary for hot water boilers with a rated power of <4.2MW.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.