The last edit to this post was made by yinkuilin6868 on 2016-2-18 at 10:34. Hazard factors during startup and preventive measures 1. Drying and baking of the hydrogenation reaction system. The purpose of drying and baking the reaction system in a hydrogenation unit is to remove moisture from within the system, eliminate free water and crystalline water present in the refractory materials of the heating furnaces, sinter the refractory materials, and thereby increase their strength and service life. When heating the furnace with coal, it is necessary to introduce fuel gas into the system; before doing so, it is essential to ensure proper airtightness and isolation of the gas. Generally, the oxygen content in the fuel gas should be less than 1%. Prevent gas leakage and migration to other systems. When lighting a heating furnace, the furnace chamber must be thoroughly purged with steam to ensure that no flammable gases remain. When heating the furnace, the temperature should be increased and decreased strictly in accordance with the specified heating curve, to avoid rapid temperature rises that could cause the moisture in the refractory materials to evaporate quickly and lead to the collapse of the furnace walls. 2. Catalyst loading in the hydrogenation reactor: Catalyst loading must be carried out strictly in accordance with the established protocol; the quality of catalyst loading has a significant impact on the operation and service life of the hydrogenation unit. Before loading the catalyst, the reactor and its internal components should be carefully inspected, as well as the condition of the catalyst dust, to determine whether the catalyst needs to be sieved. Catalyst loading is preferably carried out on dry and sunny days to ensure even distribution of the catalyst; otherwise, flow imbalances or \"hot spots\" may occur in the reactor during operation, affecting the proper functioning of the plant. When loading the catalyst, workers need to enter the reactor to carry out the work; therefore, special attention must be paid to the protection of these workers and to their safety. They must wear protective clothing and breathing masks that can supply oxygen or air. Workers entering the reactor are not allowed to bring any other items, in order to prevent foreign objects from falling into the reactor (generally, catalyst loading is carried out by professional personnel from specialized companies). 3. Purging of the hydrogenation reaction system: The purging of the hydrogenation reaction system takes place in two stages: first, the air environment is replaced with a nitrogen environment, and then the nitrogen environment is replaced with a hydrogen environment. When replacing the air environment with a nitrogen environment, it is important to note that after the replacement is complete, the oxygen content in the system should
Reply #22016-02-18
Welcome to HAIYOU to add and improve: handshake
Reply #32016-02-18
Very detailed, thank you, I’ve learned something
Reply #42016-02-18
Care must also be taken when handling DMDS to prevent leaks, and personnel should wear appropriate protective gear.
Reply #52016-02-21
During replacement, the oxygen content is required to be less than 0.2%; there’s a mistake here~
Reply #62016-02-21
There are also issues with Article 4, as the material used for the pipelines in the reaction system is austenitic stainless steel. According to Nelson’s characteristic curve, during the first start-up, when the pressure in the reaction system does not exceed 1/4 of the system’s total pressure, the lowest temperature on the reactor walls must not exceed 53 degrees; for subsequent starts-ups, this limit is 93 degrees. Article 7 requires that the speed of pressure increase and decrease shall not exceed 1.5 MPa/h.
Reply #72016-02-23
Thank you for your correction: handshake
Reply #82016-02-23
Thank you for your correction: handshake

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.