There is a Rosemount 3051 differential pressure transmitter used to measure the pressure inside the furnace. One connector is connected to the furnace itself, while the other is connected to the atmosphere. Sometimes the differential pressure stops changing; when the transmitter is removed and blown on with the mouth, the pressure changes. After it is reconnected, the differential pressure changes again. What could be causing this?
Reply #22016-03-13
The second floor is correct. The pressure tap tube or the pressure tap is blocked; blowing on it clears it.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.