Our factory uses a set of S7300 systems, with the CPU being 315-2DP. There’s a problem now, and I’d like to consult you all on it. The CPU SF and BF flash occasionally; whenever they flash, all the pumps stop, and then the pumps restart on their own once normal operation is resumed. I was wondering if there’s a communication issue, but the IM153 connector at the substation isn’t reporting any well status either. If there’s a communication issue, the data below shouldn’t be lost. Please help analyze this; I’m really stuck. Thank you
Reply #22016-03-19
BF stands for BUS FAIL, so we should still check the Profibus circuit issues. It can be connected to Step 7; in the hardware configuration, there is a diagnostic buffer.
Reply #32016-03-21
I used to use the 315-2DP+IM153 setup, and encountered similar problems; after replacing the PROFIBUS cables and MPI connectors, the issue was resolved. MPI connectors cannot be bought domestically; they must not be purchased from domestic suppliers! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! ! !
Reply #42016-03-22
I have encountered a similar problem with DP and upper-level communication: the terminal resistors were not in the ON position, which caused intermittent communication issues; even though the distance was only 1 meter, there were still problems.
Reply #52016-03-24
Is there still this problem at a distance of one meter? I welded the DB9 connector myself; it doesn’t have any termination resistors or anything, but it still works, right?
Reply #62016-03-29
It’s strange. Previously, I had two operating systems; when the terminal resistor was set to ON on one of them, powering it down would affect the data communication with the other one.
Reply #72016-03-29
It is likely due to a communication failure; one communication cycle lasts around 200 ms. Once this time limit is exceeded, the data from the distributed templates, except those in the main rack, are automatically sent back to their safe positions. By increasing the sampling frequency for analog data recordings, it is sometimes possible to observe the data returning to 0
Reply #82016-04-04
Generally, such issues are caused by soft faults. You might consider backing up the data before stopping the device, then formatting the storage card, reinstalling the software, and using software to check for any hardware errors. If there are no hardware problems, conduct an online check to see if there are any conflicts in certain settings, and consider resetting those settings.
Reply #92016-04-05
Method 1: Check the buffer information to locate the fault point and resolve the issue. Method 2: Reduce the DP rate. Method 3: Replace all DP connectors:lol
Reply #102016-04-15
The people upstairs are really reliable; thumbs up!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.