Dual level indicators are provided for hazardous liquid storage tanks

2016-04-05View Original

Thread Content

I would like to ask whether dual level indicators are necessary for hazardous liquid storage tanks? Such as an on-site level gauge, a remote transmission level gauge. Some time ago, experts who came for an inspection raised this issue, but I couldn’t find any relevant regulatory requirements. Could everyone please let me know about this standard? Thank you.
Reply #22016-04-05
SHT3007-2014 Code for Design of Tank Areas in Petrochemical Storage and Transportation Systems 6.3.2 For pressure tanks, liquid level measurement shall be equipped with one set of remote transmission instruments and one set of local indication instruments; glass plate level gauges shall not be used as local indication instruments.
Reply #32016-04-06
Our tanks are at atmospheric pressure – are there any relevant regulatory requirements?
Reply #42016-04-06
This post was last edited by altpage on 2016-4-6 10:44
Reply #52016-04-08
Now, flammable liquid storage tanks must be equipped with high liquid level alarms, so there is one on-site alarm and one for remote monitoring.
Reply #62016-04-09
Is there any specification that explicitly requires this?
Reply #72019-06-22
As we mentioned during today’s inspection as well, liquid storage tanks require a dual-level monitoring system; there is no basis for not doing so
Reply #82019-06-22
Refer to: GB17681-1999 Technical Requirements for Acceptance of Safety Monitoring and Early Warning Systems in Flammable and Explosive Tank Areas, 5.5 Liquid storage tanks must be equipped with level detection instruments, and at least two different types of such instruments shall be installed in each tank.
Reply #92019-06-22
Liquid storage tanks must be equipped with dual level indicators, primarily for dual protection – so that if one of the level indicators malfunctions, the other can take over temporarily.
Reply #102021-06-24
For details, see SH3007 Design Specifications for Storage and Transportation Systems in Petrochemical Enterprises, 6.3.2
Reply #112021-06-25
It mainly refers to large storage tanks, but these days it is considered unreasonable to require double ones for just any storage tank~~~~

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.