Are the outlets of the safety valves connected together without any reduction in diameter, and is this in compliance with the specifications?

2016-04-08View Original

Thread Content

I have a question now: For a customer’s liquefied petroleum gas storage tank, the outlets of the two safety valves are connected together without any reduction in diameter. Is this in compliance with the regulations?
Reply #22016-04-08
Two safety valves are considered, one in use and one as a backup; the discharge capacity of each valve is sufficient to meet the overpressure requirements, therefore there is no need for a change in the diameter of the outlet pipe.
Reply #32016-04-08
Agree with the second floor – the safety valves operate in a one-in-use and one-backup configuration; it’s not necessary to change the diameter, but the pipe diameter should be calculated based on the pressure drop in the main pipeline.
Reply #42016-04-08
It meets the specifications; they come in one active unit and one standby unit.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.