Pipeline issues in vertical tanks

2016-04-21View Original

Thread Content

A vertical atmospheric pressure tank is used to collect the condensate water from the steam heat exchanger. Should the condensate pipe extend below the liquid level? Will this cause excessive vibration? If it is extended below the liquid surface, should a elbow be added at the lower part of the tube, or should it be open directly facing the bottom of the tank? Which approach is better?
Reply #22016-04-21
This depends on the normal operating level and the low-low level of the equipment; the water pipe should extend below the low-low level, and there is no need to use elbows.
Reply #32016-04-21
If the condensate is recovered in a closed system, there is no need to extend it below the liquid surface. Under these operating conditions, the condensate usually contains a certain amount of steam, and extending it underwater can easily cause water hammer.
Reply #42016-04-21
It is recommended to extend it below the liquid surface, but a fixed support must be installed
Reply #52016-04-21
Is the condensate collection tank open?
Reply #62016-04-22
Our standard practice here is to insert the nozzle 100-150mm into the upper head
Reply #72016-04-23
The condensate enters the storage tank (or buffer tank) above the liquid level, which allows for vapor-liquid separation or flashing to occur.
Reply #82016-04-23
Are there any relevant regulatory requirements?
Reply #92016-04-25
Not really; it’s just a judgment based on work experience

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.