Technical assistance: A 250KW high-voltage motor has an insulation resistance of 20 megohms – is it safe to start it?

2016-04-28View Original

Thread Content

This post was last edited by hesonchang214 on 2016-4-30 at 14:45. The insulation resistance of the 250KW high-voltage motor is 20 megohms – is it safe to start it? 10KV
Reply #22016-05-04
For a generous approach, a standard of 1 kV per 1 meter is sufficient.
Reply #32016-05-07
Ahah, it should work fine to start it! But the insulation resistance is still low; in cases of poor weather conditions (such as rainy days), it is still acceptable. If the weather is clear, the insulation resistance is low; it’s best to check and address the wiring of the motor cables.
Reply #42016-05-24
Isn’t the standard that 1 KV corresponds to 1 megohm? It can be activated
Reply #52016-06-14
Start it without any problems, run it for a while, and check the changes in insulation resistance.
Reply #62016-06-19
It can be started; it is recommended to use a value of over 60 megohms for starting

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.