The water in the cooling circulation tank has turned red, but the iron ion level is not high. The fill material in the cooling tower was replaced last winter, and the water started to turn red in April this year; both the water quality and bacterial counts are normal. I’m not sure what could be the cause I’m asking for help from all the experts!
Could some material have gotten in? Is there pH monitoring?
Recommendation: Analyze whether the iron ion content in the water quality is high; normal maintenance levels are below 1 mg/L. It is advisable to provide data on both the added water quality and the circulating water quality, as well as continuous monitoring of the water quality, in order to rule out color changes caused by the water quality; At the same time, check whether there are any other media leaking into the system, and determine if this is due to the leakage
1. Comprehensive analysis of water quality for replenishment and circulating cooling water. 2. Consideration of iron ions and microbial algae. 3. Inspection for leaks due to material leakage and reactions in the water body. 4. Drainage replacement and activation of the bypass filtration system
With a large amount of iron ions, the entire water body turns red. Organic substance leaks, methanol, and ammonia nitrogen leaks can also cause microbial growth to turn red.