The Yamata AVP103 locator that was recently debugged has good self-tuning capabilities, but there is still air output at 4 mA. What’s going on?

2016-05-09View Original

Thread Content

The Yamata AVP103 locator that was recently debugged has good self-tuning capabilities, but there is still air output at 4 mA. What’s going on? The valve always has a slight opening, and its linear performance is not good. How to solve this?
Reply #22016-05-09
Adjust it slowly; there should be a way to make fine adjustments
Reply #32016-05-09
At 4mA, the positioner is adjusted so that its zero point is reached, resulting in an output of zero.....
Reply #42016-05-10
Hold down the UP or DOWN button; once the output becomes 0, the locator will remember it on its own.
Reply #52016-05-10
Do I need to adjust it again after making the changes?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.