What are the reasons why the temperature measured by B-type fiber optic sensors is displayed as 0 in the DCS?

2016-05-23View Original

Thread Content

Is it possible that the positive and negative terminals are reversed?
Reply #22016-05-23
First, check whether there is an open circuit in the thermocouple cable!
Reply #32016-05-23
This post was last edited by wojiuy2y2 on 2016-5-23 13:41. What signals does the DCS terminal wiring module receive?
Reply #42016-05-23
Use a multimeter to measure the mV value output by the thermocouple; a value of 0 mV may indicate an open circuit in the thermocouple, or a fault in the display section.
Reply #52016-05-23
Based on your description, it’s unlikely that a single thermocouple wire is damaged or that there’s an issue with the circuit, as you have 6 of them installed; it would indeed be worth checking to see if the wiring is connected incorrectly

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.