24v instrument power supply issue

2016-06-14View Original

Thread Content

This post was last edited by hfrs on 2016-6-15 at 16:46. 500 meters, 24vdc, for electromagnetic flowmeters and mass flowmeters; powered by 2x1.5 cables. Has anyone used this? Do I need to replace the 2x2.5 cable?
Reply #22016-06-14
I’ve used it; the voltage rose to 17.5 volts, and then I started to get headaches. There are so many instruments that it’s not possible to get rid of any of them.
Reply #32016-06-14
We have never used 2x2.5 cables for power supply; we use 2x1.5 cables for that purpose
Reply #42016-06-15
A 2x2.5 cable should be used.
Reply #52016-06-15
I’ve used it; a 1.5 value works fine for such a long distance, but the interference is quite severe. It’s better to use 2.5, as there is signal attenuation and voltage drop
Reply #62016-06-15
500 meters is quite far; the voltage drop is too large, so it’s better to use a thicker wire. 2x2.5
Reply #72016-06-15
It is recommended to use 2×2.5. There is a common rule regarding this; I’ve forgotten whether it’s a standard requirement or one of our own regulations. It seems that for distances over 300 meters, a 2.5 gauge cable must be used, so we decide to use 2.5 gauge cables for all our designs, even though the signal cables only require a 1.0 gauge
Reply #82016-06-15
It is recommended to use 2*2.5, to facilitate maintenance and error diagnosis of the instruments in the future
Reply #92016-06-15
The distance is too great; it’s best to calculate the voltage drop, and it could be changed to 220V.
Reply #102016-06-15
A 4-20 mA signal uses 1.5, while mass flow meters are powered by AC; DC power results in too long distances and significant voltage drop.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.