Regarding the pressure transmitter response time

2016-06-15View Original

Thread Content

When the design institute requires that the transmitter’s response time not exceed 50 milliseconds, does it refer to the damping time? There’s no description of the response time in the manufacturer’s manual?
Reply #22016-06-15
These two are not the same thing. The damping time of an instrument is generally defined as the time during which the amplitude of the signal from the measured quantity as it reaches the reading indicator does not exceed 1% of the total scale length. Response time is generally defined as the time it takes for the sensor to reach 90% of the final value after the test quantity changes by one step. However, 50 milliseconds is indeed a very small value; ordinary Romon series models cannot meet this requirement
Reply #32016-06-15
It’s likely a mistake in the number; it should be 500ms.
Reply #42016-06-16
I also wonder why the voltage transformer needs to be so sensitive...
Reply #52016-06-16
The response time of pressure transmitters may also be affected by the length and diameter of the pressure conduit.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.