HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Does the pressure transmitter need to be relocated?

2016-06-25View Original

Thread Content

For single-flange pressure transmitters with a capillary, ranging from 0 to 20 kPa, is it necessary to perform calibration? The transmitter is installed two meters below the flange opening.
Reply #22016-06-25
Theoretically, migration is required. Calculating numerical migration is not recommended. However, the recommended method for migration is as follows: 1. Empty the tank, install the single-flange pressure transducer, fix the gauge head, adjust the range, and then perform zero calibration. 2. With the contents inside the tank, after fixing the gauge head, secure the flange with screws (but do not tighten them) in order to calibrate the zero point of the range.
Reply #32016-06-25
For single-flange types, installation below the pressure tapping point is required; this involves positive migration. A drop of two meters is too much – if the range is small, it may not be possible to carry out the migration
Reply #42016-06-27
Based on the density of the measuring medium, the pressure difference at a height of 2 meters is calculated, and this value is then subtracted (resulting in a negative migration). If measurements are taken without performing a zero-point adjustment, the pressure reading is the sum of the pressure of the medium inside the container and the capillary pressure (P1+P2). Calculation formula: P=hgρ
Reply #52016-06-27
It must be migrated. The method is as described on the 2nd floor.
Reply #62016-06-27
A migration is needed. I agree more with the first method described on the second floor; I didn’t understand the second one – how can one remove the flange when there is material inside the tank?
Reply #72016-06-27
Migration is definitely necessary; the zero point of the gauge does not match the actual pressure zero point. Since the gauge is installed below the pressure sampling point, it needs to be shifted forward
Reply #82016-07-17
The measured pressure is too low; migration is necessary. At a height of 2 meters, there is almost 20 KPa of pressure, so without migration the measured pressure will not be accurate; In daily life, we rarely transfer stress, because the stress is much greater than the amount that can be transferred, so it goes unnoticed ; We should calculate the setting point of the gauge using the density of silicone oil (the typical density for silicone oil is 0.94), or we can hang the flange at the installation point with the gauge face facing backward in order to read the values ; Under normal conditions, the gauge reading is around -19 KPa. We can simply set the gauge to range from -19 to 1 KPa (the exact value should be calculated accordingly)
Reply #92016-07-17
It’s equivalent to recalibrating at zero point; you could also call it migration. I’m not sure if that’s correct – looking forward to discussions

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.