How to configure the addition of analog inputs on the wcc+s7300

2016-06-26View Original

Thread Content

At a construction site belonging to one company, the wiring of four-wire electromagnetic flowmeters from the field area to the control room has been completed. However, configuration is not yet possible. I took a quick look and saw that there are analog input points available in the PLC configuration, but they are based on a two-wire system. So, how should the WCC and PLC be configured, how should they be connected, and how can variable information from the field device be retrieved? If it is necessary to display cumulative flow rates, can this be achieved using only the WCC?
Reply #22016-06-26
I’m not sure if your AI card is 7KF02; the four-wire configuration needs to be set by adjusting the signal module on the side. Then, in STEP 7, convert the PIW corresponding to the AI channel to a flow range value using FC105, and assign that value to MD. Create a variable for the MD communication point in WINCC, and then connect this variable to the input/output fields in the WINCC configuration screen.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.