On the use of the S7-400 simulation software S7-PLCSIM

2016-07-27View Original

Thread Content

When I use S7-PLCSIM in STEP7, I turn on the simulation switch and download the program to the simulated CPU; in both cases the CPU shows as not connected. May I ask if it is necessary to set the interface type when using simulation software? How can a program be downloaded to a simulated CPU to simulate it?
Reply #22016-07-28
Yes! SET PG/PC needs to be configured; refer to your network connection method.
Reply #32016-07-28
Open set pg-pc interface; generally, setting it to plcsim (mpi) is sufficient. The value within the parentheses can be mpi, tcp-ip, or iso – with mpi being the most convenient option

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.